Jaros said:
I have a 200W flexipanel solar sheet as well as 520W of bifold solar and sometimes think it's worth an extra AGM via MPPT/ 2000W inverter just to run these power hungry monsters we have today. The panel would only be used to keep charge up on the AGM-waddaya think??
The key to running an inverter is;
1. Regardless of invert actual size i.e. you might have a 2,000W inverter, but only ever use 1,200W from it. The key figure is then 1,200W unless you think of running something else at the same time within the inverter limit.
2. Then you need a battery bank big enough to run it i.e as in my previous post 240AH (for 1,200W) or 400AH for 2,000W.
3. Then you need to work out how long you use the inverter for to calculate the AH used.
4. Then you need to work out, in a worst case scenario, how much solar you need to replace what you use. I use a rule of thumb, 4 times the AH used in panel W.
i.e. as mentioned I use around 35-40AH daily, sometimes more, sometimes less, 4 x 40AH =160W in panel. I then added 25% contingency = 200W.
I've seen days in VIC earlier this year, where it was crap weather all day and I was only getting 2-3 amps from my 200W, which will not replace all I use and I have very good panels. Which as I have noted in other threads is why I have other charging options, just in case.
The above figures are given, with getting a reasonable life cycle from your battery/ies, in mind.